I have discovered a fault with my logic. Last night the battery temperature just dipped to 5C. One only bms went to low temp fault. It will stay there until 10c or until I manually reset it. It was 8 C when I switched on the ignition hoping to start heating. Of course my temp sensor from the switch had missed the below 5.5C period so at 8C it saw no need to heat.I have successfully heated my battery from cold until the bms were satisfied and charging began. I know now that my pads take 12 amps whilst heating. My bms will be set to 5C but they have a lag so must be heated to 10C to loose the low temp fault setting. My cells under my heating regime are about 1 degree C cooler on the none heated side compared to the top of the heated side. So it is best to site the bms thermistors ontop of the heat pads. My heat pads are between each pair of 100ah cells.
It took 9 minutes to heat the cells from 6C to 10C using about 2Ah of battery. If the ambient was just 5C it would take about 11 minutes to get to charging temp. If the ambient was 0C it would take 22 minutes.
I have set the w1209 temp switch to a backlash of 6.5 degree, with a temperature to switch off the relay of 12C. That means that it will instigate charging at 5.5C to ensure it is set before the bms go to fault at 5C. When I switch the ignition on charging will begin and switch off at 12C by which time the bms sensors will be at 10C and ready to charge. Then I can start the engine to recharge immediately. Only the first relay coil will drain the starter battery, all other load is from the leisure battery. I will gain back the 2Ah of heating loss from the batteries in just over 2 minutes of running the engine.
I can still use my ring solar controller for solar, but it cannot charge or heat the batteries when it is cold. I will see how often there is enough solar charging opportunity lost before I try to deal with that.
I'm glad I'm not there yet, work has gone silly. Unfortunately that pays the bills. I guess I'll be needing more pennies when I start the self build electric motorhomeI have discovered a fault with my logic. Last night the battery temperature just dipped to 5C. One only bms went to low temp fault. It will stay there until 10c or until I manually reset it. It was 8 C when I switched on the ignition hoping to start heating. Of course my temp sensor from the switch had missed the below 5.5C period so at 8C it saw no need to heat.
So either I need to rewire the temp sensor to be always on, a power drain of around 1ah per day all year, or I must reduce the temp backlash to say 1.5C so that it switches on heating at anything below 10.5C (at ignition on) and switches off at 12C ensuring that the bms will be able to charge, whatever the temperature at ignition on. That means I will heat much more frequently but the new heating occasions may only be perhaps 1ah. Just before I have ample recharge available. Decisions?
If you are talking to me, I guess you are, then the answer is no. I set the low temp charge cut off to 5C when the sensor notes a temperature below 5 it goes into a low temp fault mode and no charge can come in. I have tested that with a clamp current meter. I can still use the battery as there is a different low temp discharge setting that I set to -20C.Not sure if I have missed something but does your set up not work in the same way commercially built Lifepo4 battery do? I can put as much charge as I can throw at them realistically down to minus 5, from minus 5 to zero I can still charge but at a reduced rate. In any event I can carry on discharging safely to minus 20
A good BMS will have a setup where it will not allow a charge current to come into the battery when it is below a selected current. If you have that feature, then there really should be no need to add in external circuitry to disable or disconnect chargers.Not sure if I have missed something but does your set up not work in the same way commercially built Lifepo4 battery do? I can put as much charge as I can throw at them realistically down to minus 5, from minus 5 to zero I can still charge but at a reduced rate. In any event I can carry on discharging safely to minus 20
I agree with what you say. We were talking about a victron mppt and you said that cutting the mppt output away from the battery and diverting it's output to battery heaters as you describe here would be a use as a power source rather than a battery charger and would invalidate the guarantee. Were we talking at cross purposes?It is a much better idea - IMHO - to fit a BMS that manages the charging disconnects internally, or if your chosen BMS does not have that ability, to not attempt to control the chargers, but use a temp sensor to control a power relay to cut the charging circuit TO the battery and just leave the load circuit FROM the battery active (would be a little more tricky with something like a Victron Multiplus to do that, but it is possible).
No, it wouldn't invalidate the guarantee/warranty. What Victron says is that it can be used that way but they won't guarantee it will actually operate successfully for everyone.I agree with what you say. We were talking about a victron mppt and you said that cutting the mppt output away from the battery and diverting it's output to battery heaters as you describe here would be a use as a power source rather than a battery charger and would invalidate the guarantee. Were we talking at cross purposes?
It is relevant again as my ring b2b is throwing another wobbly and I might give up on it.
Sorry folks, not sure if I had missed my meds when I typed this but I made a glaring error each time I put minus 5, it should have just been plus 5 then reduced rate charging to zero and safely discharge to minus 20.Not sure if I have missed something but does your set up not work in the same way commercially built Lifepo4 battery do? I can put as much charge as I can throw at them realistically down to minus 5, from minus 5 to zero I can still charge but at a reduced rate. In any event I can carry on discharging safely to minus 20