wildebus
Forum Member
Trying to do something and what is happening is not very logical and I am wondering if I am missing something, so if anyone has any ideas ....
So the goal ... I want to add control to a setup in order to stop a Lithium Battery charging when it is below a certain temperature.
I bought a Temp Controller that has a Relay that will either be open or closed depending on the temperature the temp probe is reading.
The B2B Charger (Victron Orion) has a 2-pin remote input that means it will only be allowed to operate if the two pins are shorted
The Mains Charger (Multiplus) has exactly the same arrangement on an remote/auxiliary feed input.
So the theory is that if I connect the two pins of the charger to the two pins of the Temp Controller, when the relay closes, the Remote input is shorted and the charger is allowed to work.
This is the effect of the remote input on the Multiplus
First the Remote/Aux input is left closed (two pins connected)
And when it is open (two pins not connected together)
(Passthru means there is AC power into the Multiplus but nothing going to the batteries)
The two screenshots above were taken when connected to the Temperature Controller and turning its relay on and off.
I can control the B2B charger in exactly the same way and it works as well. So what is the quandary?
Well, I want to be able to control both Chargers as want no charging from either source when the temp is low. And both chargers are controlled the same - short pins to enable, open pins to disable.
But when I connect both sets of wires together - one of each charger to one side of the relay, and the other wires of each charger to the other side of the relay - there is an automatic short somehow even when the relay is open. But if only one of the chargers is connected to the Temp Controller, it works correctly.
Now there is a workround I am pretty sure I could use with extra hardware and would only cost an extra £3 or so, but extra hardware equals more potential failure points so would prefer not to.
I did try connecting both charger remote inputs in a ring - so the wire would go "RELAY OUT" -> "B2B 1"; "B2B2" -> "MP1"; "MP2" -> "RELAY IN".
That way, when the relay is closed the ring is made and the pins of each are connected, just in a longer route.
Doing this resulted in the B2B having the remote control as wanted, but the Multiplus never being allowed to work.
Is there something I am missing on why this is not working? not applying any voltage to anything, just really based on a connection going short-circuit/low resistance.
So the goal ... I want to add control to a setup in order to stop a Lithium Battery charging when it is below a certain temperature.
I bought a Temp Controller that has a Relay that will either be open or closed depending on the temperature the temp probe is reading.
The B2B Charger (Victron Orion) has a 2-pin remote input that means it will only be allowed to operate if the two pins are shorted
The Mains Charger (Multiplus) has exactly the same arrangement on an remote/auxiliary feed input.
So the theory is that if I connect the two pins of the charger to the two pins of the Temp Controller, when the relay closes, the Remote input is shorted and the charger is allowed to work.
This is the effect of the remote input on the Multiplus
First the Remote/Aux input is left closed (two pins connected)
And when it is open (two pins not connected together)
(Passthru means there is AC power into the Multiplus but nothing going to the batteries)
The two screenshots above were taken when connected to the Temperature Controller and turning its relay on and off.
I can control the B2B charger in exactly the same way and it works as well. So what is the quandary?
Well, I want to be able to control both Chargers as want no charging from either source when the temp is low. And both chargers are controlled the same - short pins to enable, open pins to disable.
But when I connect both sets of wires together - one of each charger to one side of the relay, and the other wires of each charger to the other side of the relay - there is an automatic short somehow even when the relay is open. But if only one of the chargers is connected to the Temp Controller, it works correctly.
Now there is a workround I am pretty sure I could use with extra hardware and would only cost an extra £3 or so, but extra hardware equals more potential failure points so would prefer not to.
I did try connecting both charger remote inputs in a ring - so the wire would go "RELAY OUT" -> "B2B 1"; "B2B2" -> "MP1"; "MP2" -> "RELAY IN".
That way, when the relay is closed the ring is made and the pins of each are connected, just in a longer route.
Doing this resulted in the B2B having the remote control as wanted, but the Multiplus never being allowed to work.
Is there something I am missing on why this is not working? not applying any voltage to anything, just really based on a connection going short-circuit/low resistance.