Slightly confused by the results.
My understanding was the nearer to unity (1) the Pk value was the greater the efficiency hence battery longer battery life?
I realise it’s more complicated than that, just the results seem to be the opposite to what I would have expected?
Not sure what you are meaning by efficiency, or battery life with respect to the Peukert exponent value.
What this result indicates is that as you change the Value, the SOC calculation alters, as it recalculates how the draw current level affects the capacity.
Now if is hard to actually say the results are the way you would expect or opposite to them. Reason being you don't know the type of current this system has been drawing
If I were drawing a tiny current all the time, then the capacity would be greater then the "headline" one the battery maker quotes. if I were drawing a big current all the time, then the capacity would be lower than quoted.
The larger the value over 1, the greater the capacity is impacted by current draw level (and a value of 1.00 means there is no effect).
So to explain further ...
I think the following is why when I lowered the value (which would indicate the effect on the battery of drawing different current rates is lessened), the SOC dropped.
The value it was at - 1.10 - would tell the monitor the battery had a certain Peukert Factor.
By reducing the value, it is saying the effect of different current rates is not as pronounced as previously stated (with the 1.10 setting). Remembernthr closer to 1.00, the less the effect.
This means that the monitor had been until then, exaggerating the benefit (in terms of greater capacity) of low current rates and conversely, being overly pessimistic on high current rates.
The fact the the SOC went down when I lowered the Peukert Exponent value suggests that my current rate was on average below C20 (the battery capacity you set in the BMV is the makers C20 value), and so the benefit of lower current rates was previously calculated too 'generously'.
If, however, the SOC went UP when I lowered the Peukert value, which is equally possible, then it would be because the average current was ABOVE the C20 rate and the calculation was too pessimistic.
In this particular case, the result makes sense.
By lowering the value I am telling the BMV that the battery is not as affected by current rates as the 1.10 exponent would suggest;
The system has being drawing around the 1.0 to 1.5A range for days and days (and the C20 rate for this bank is 15A)
The SOC reduces as the average current is under C20.
So all the above tie up together. The key thing is IS IT RIGHT?
The logic follows but it doesn't tell you if the actual number is right. And that is down to the operator.
And why I compared the SOC with the Voltage.... This is a brand new setup and needs tuning in. When I looked at the SOC and at the voltage, they didn't really match closely enough... The SOC looked too high. I knew I had a pretty low current draw and concluded that the Peukert Exponent value was not right for this battery bank (the BMV fitted has been on a bunch of different batteries so no surprise it needed settings altered).
If you have the data sheets for your battery, showing the different capacities at different C rates, you can actually plug that info into a Peukert Exponent calculator Victron have on their website and that will give you a number to put into the BMV in fact.
If you don't have the data, then you can do similar to what I did in this case and use some judgement and logic to tweak the number.