Inverter Earthing:
Having just fitted my Victron 12/500 Phoenix inverter and tested it, there was just one thing that I needed to sort. Using my trusty plug-top Socket Tester it always showed an earth fault, and so it should as the earth configuration from the inverter does not resemble our UK domestic supply. In the UK Neutral and Earth are similar both being connected to earth back at the substation. The Victron inverter is delivered with the 'UK 3 pin socket' the earth is floating (sort of) hence the Socket Tester showing a fault.
As delivered, Victron probably expect you use their inverter with Class 2, Double Insulated appliances so the earth pin is redundant.
Put the inverter in a motorhome and plug in a fridge, microwave, toaster which are Class 1 appliances and not be Double Insulated, now what?!
The Victron instructions below give the option to ground the Neutral by moving the link as shown. This clears the Earth Fault condition on the Socket Tester.
Without the Earth and Neutral lines being connected together will your van RCD work in the event of a fault (if using the vans 13 Amp sockets)? Fried wife my be hard to explain!
The inverters ground terminal can be connected to the vehicle chassis ground: But should it? Victron also say "the chassis must be connected to a reliable ground".
What consideration do other inverter users give when using their inverter and does it meet with Local Regulations?
Now, don't ask me, I'm a simple electronics engineer (retired) and these days consider anything over 3v3 highly dangerous.
Having just fitted my Victron 12/500 Phoenix inverter and tested it, there was just one thing that I needed to sort. Using my trusty plug-top Socket Tester it always showed an earth fault, and so it should as the earth configuration from the inverter does not resemble our UK domestic supply. In the UK Neutral and Earth are similar both being connected to earth back at the substation. The Victron inverter is delivered with the 'UK 3 pin socket' the earth is floating (sort of) hence the Socket Tester showing a fault.
As delivered, Victron probably expect you use their inverter with Class 2, Double Insulated appliances so the earth pin is redundant.
Put the inverter in a motorhome and plug in a fridge, microwave, toaster which are Class 1 appliances and not be Double Insulated, now what?!
The Victron instructions below give the option to ground the Neutral by moving the link as shown. This clears the Earth Fault condition on the Socket Tester.
Without the Earth and Neutral lines being connected together will your van RCD work in the event of a fault (if using the vans 13 Amp sockets)? Fried wife my be hard to explain!
The inverters ground terminal can be connected to the vehicle chassis ground: But should it? Victron also say "the chassis must be connected to a reliable ground".
What consideration do other inverter users give when using their inverter and does it meet with Local Regulations?
Now, don't ask me, I'm a simple electronics engineer (retired) and these days consider anything over 3v3 highly dangerous.