Forum Member
Grappling with a slight quandary on which product to buy for my Motorhome....
Going to get a Victron Multiplus, with the intention that it will charge the batteries (LiFePO4 Lithium Bank) and also provide 240V power for stuff like Electric Hob, Instant Pot, 3-way Fridge and Water Boiler - all those dependant on how much battery power I have available of course. Oh, and plus a Hairdryer I would imagine!
Now nothing in that list is above around 1200W - Hob maybe 800W, Instant Pot 900W, Fridge 200W, Boiler 850W - so the Multiplus 12/2000 would be a perfectly usable solution
There is also one other 240V item I haven't mentioned and that I wouldn't want to run off the batteries at all - the Gas/Mains Space Heater. This can be selected to run at 500W, 1000W or 2000W.
Now the quandary ... If you are on a hookup and you put the heater on say 2000W as you want some heat and you are paying for the hookup anyway, and then you turn on say the hob, you could overload the Hookup and trip the breaker. Annoying and inconvenient.
If you get a Multiplus 12/3000, that has two 240V Outlets - one that essentially goes through the inverter part - so could be used for the Hob, Fridge, etc when not on hookup, and another outlet that is only active when hooked up - so that would feed the Space Heater and no danger of running the heater when no mains
The key thing about having the Mains only outlet on the Multiplus rather than just 'alongside' and independant of the Multiplus is that the total current draw from the mains hookup is monitored - and so if you set the current limit at say 10A due to a limited site EHU, when the heater is running at 2000W and you turn on the 800W hob, the maximum current drawn from the mains will not be 2800W (2000 boiler + 800 Hob) but 2400W (240V x 10A) and the 400W difference will come from the Battery using the "Power Assist" feature of the Multiplus.
If the Space Heater is powered on a line outside of the Multiplus, it will have no knowledge of the current draw and the power assist feature won't work properly
So the 12/3000 is the better product. but it costs over £200 more. It has a bigger inverter capability and bigger charger as well, but the 12/2000 ones are big enough really for my needs, so it is down to the question of is the ability to monitor and control the EHU current worth the extra dosh?
opinions on a e-postcard ....
Going to get a Victron Multiplus, with the intention that it will charge the batteries (LiFePO4 Lithium Bank) and also provide 240V power for stuff like Electric Hob, Instant Pot, 3-way Fridge and Water Boiler - all those dependant on how much battery power I have available of course. Oh, and plus a Hairdryer I would imagine!
Now nothing in that list is above around 1200W - Hob maybe 800W, Instant Pot 900W, Fridge 200W, Boiler 850W - so the Multiplus 12/2000 would be a perfectly usable solution
There is also one other 240V item I haven't mentioned and that I wouldn't want to run off the batteries at all - the Gas/Mains Space Heater. This can be selected to run at 500W, 1000W or 2000W.
Now the quandary ... If you are on a hookup and you put the heater on say 2000W as you want some heat and you are paying for the hookup anyway, and then you turn on say the hob, you could overload the Hookup and trip the breaker. Annoying and inconvenient.
If you get a Multiplus 12/3000, that has two 240V Outlets - one that essentially goes through the inverter part - so could be used for the Hob, Fridge, etc when not on hookup, and another outlet that is only active when hooked up - so that would feed the Space Heater and no danger of running the heater when no mains
The key thing about having the Mains only outlet on the Multiplus rather than just 'alongside' and independant of the Multiplus is that the total current draw from the mains hookup is monitored - and so if you set the current limit at say 10A due to a limited site EHU, when the heater is running at 2000W and you turn on the 800W hob, the maximum current drawn from the mains will not be 2800W (2000 boiler + 800 Hob) but 2400W (240V x 10A) and the 400W difference will come from the Battery using the "Power Assist" feature of the Multiplus.
If the Space Heater is powered on a line outside of the Multiplus, it will have no knowledge of the current draw and the power assist feature won't work properly
So the 12/3000 is the better product. but it costs over £200 more. It has a bigger inverter capability and bigger charger as well, but the 12/2000 ones are big enough really for my needs, so it is down to the question of is the ability to monitor and control the EHU current worth the extra dosh?
opinions on a e-postcard ....