I hope I've got this right...
I've been sizing the battery bank for my hopeful build and reluctantly gone away from all-electric (winter heating...) so it's a more conventional load calculation.
Before I started I thought it was mostly about straight Ah capacity, but I now realise it can also be about peak current draw if you're planning any big currents.
One of the things I need to support is a 2kw hair dryer. This seems to driving my inverter size, but I'm thinking the impact of its current draw on the battery bank needs to be checked. I need about 240Ah energy capacity for my target of 2 days off-grid so I could meet that with 2 x 120Ah batteries, but will 2 batteries manage the current draw of the hair dryer? I think 'yes' because:
The hair dryer is actually rated at 1800W and I'm not sure that my wife uses it full power all the time, but on the other hand, I don't know the power factor either. So to be conservative, let's stick with 2000W and convert directly to12V - about 166A. Add an overhead for the inverter of 15% and we get around 190A. If my batteries are perfectly matched that would be 95A per battery.
I found a spec for some Leoch 120Ah Leisure batteries and the CCD table shows that 95A would give me around 20-30 minutes discharge time for a final voltage of around 1.7/cell. Since the hair dryer is on for 5 minutes typically, we would only be 5/20th=25% worst case discharged at the end of it. So all happy?
Am I on the right lines with this? One query is how to interpret the CCD table - it gives a choice of FV figures from 1.85 to 1.6. Not sure what that means.
Thanks!
I've been sizing the battery bank for my hopeful build and reluctantly gone away from all-electric (winter heating...) so it's a more conventional load calculation.
Before I started I thought it was mostly about straight Ah capacity, but I now realise it can also be about peak current draw if you're planning any big currents.
One of the things I need to support is a 2kw hair dryer. This seems to driving my inverter size, but I'm thinking the impact of its current draw on the battery bank needs to be checked. I need about 240Ah energy capacity for my target of 2 days off-grid so I could meet that with 2 x 120Ah batteries, but will 2 batteries manage the current draw of the hair dryer? I think 'yes' because:
The hair dryer is actually rated at 1800W and I'm not sure that my wife uses it full power all the time, but on the other hand, I don't know the power factor either. So to be conservative, let's stick with 2000W and convert directly to12V - about 166A. Add an overhead for the inverter of 15% and we get around 190A. If my batteries are perfectly matched that would be 95A per battery.
I found a spec for some Leoch 120Ah Leisure batteries and the CCD table shows that 95A would give me around 20-30 minutes discharge time for a final voltage of around 1.7/cell. Since the hair dryer is on for 5 minutes typically, we would only be 5/20th=25% worst case discharged at the end of it. So all happy?
Am I on the right lines with this? One query is how to interpret the CCD table - it gives a choice of FV figures from 1.85 to 1.6. Not sure what that means.
Thanks!